Classic 150's charge times not resetting at night
« on: February 16, 2017, 02:01:41 PM »
I have (2) 150's set up in "follow me" mode.  Within the last few weeks I noticed that the master 150 was not consistently resetting in the evening during the resting phase.  Any ideas why this has started happening?  I am running firmware 1933 (01/08/2015).

Westbranch

  • Hero Member
  • *****
  • Posts: 2323
  • Building System (sort of) 1 weekend at a time
Re: Classic 150's charge times not resetting at night
« Reply #1 on: February 16, 2017, 02:20:38 PM »
Well I looked and they are up to V. 2126....  an update never hurts...

http://www.midnitesolar.com/firmware.php?firmwareProduct_ID=1
CL647 asleep
KID 51(B) FW1811 560W C&D 24V 900Ah AGM
CL 29032 FW V.2096-NW2097-GP? 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
Linksys Wet54g Bridge NetGear DS104Hub, ASUS RTN10 rter,
Hughes 1100 Modem
Cotek ST1500 Inv, Omnicharge 3024  Eu3/2/1000i Gens
West Chilcotin, BC 1680 watts to come

Rejuvenation Farm

  • Newby
  • *
  • Posts: 14
Re: Classic 150's charge times not resetting at night
« Reply #2 on: February 16, 2017, 03:06:54 PM »
I plan on updating soon.  Not sure why that would be the cause of this issue though.  It has been working great for the past year or so and nothing has changed on my end that would impact the CC's.

Westbranch

  • Hero Member
  • *****
  • Posts: 2323
  • Building System (sort of) 1 weekend at a time
Re: Classic 150's charge times not resetting at night
« Reply #3 on: February 16, 2017, 03:38:38 PM »
have you tried a VMM?  alias a Factory Reset?

Power down PV then Battery, press both L &  Right soft keys and while holding the keys IN then Power up the BATTERY , you should hear the fans test and shut off then the MNGP screen comes alive... now release keys... RESET all settings, if you saved them ...

enjoy
CL647 asleep
KID 51(B) FW1811 560W C&D 24V 900Ah AGM
CL 29032 FW V.2096-NW2097-GP? 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
Linksys Wet54g Bridge NetGear DS104Hub, ASUS RTN10 rter,
Hughes 1100 Modem
Cotek ST1500 Inv, Omnicharge 3024  Eu3/2/1000i Gens
West Chilcotin, BC 1680 watts to come

Rejuvenation Farm

  • Newby
  • *
  • Posts: 14
Re: Classic 150's charge times not resetting at night
« Reply #4 on: February 16, 2017, 03:50:22 PM »
I have not tried the factory reset - I will give it a go this evening.  I have been physically powering the units off using the breaker switch on my inverter to reset the charge times. 

Westbranch

  • Hero Member
  • *****
  • Posts: 2323
  • Building System (sort of) 1 weekend at a time
Re: Classic 150's charge times not resetting at night
« Reply #5 on: February 16, 2017, 04:02:20 PM »
I power down both, as above, and then let it rest for  up to 1 minute.... and always power the PV on last. 
Sounds like you did not shut them both off...??
CL647 asleep
KID 51(B) FW1811 560W C&D 24V 900Ah AGM
CL 29032 FW V.2096-NW2097-GP? 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
Linksys Wet54g Bridge NetGear DS104Hub, ASUS RTN10 rter,
Hughes 1100 Modem
Cotek ST1500 Inv, Omnicharge 3024  Eu3/2/1000i Gens
West Chilcotin, BC 1680 watts to come

Rejuvenation Farm

  • Newby
  • *
  • Posts: 14
Re: Classic 150's charge times not resetting at night
« Reply #6 on: February 16, 2017, 08:45:18 PM »
Yes - I have manually shut both down a half dozen times now hoping it would fix the issue.  Sometimes I will go nearly a week with them resetting normally, then as soon as I drop my guard, I get burned.  I never had this issue before - it just popped up out of the blue.

Vic

  • Hero Member
  • *****
  • Posts: 1614
Re: Classic 150's charge times not resetting at night
« Reply #7 on: February 16, 2017, 10:00:39 PM »
   ...   Within the last few weeks I noticed that the master 150 was not consistently resetting in the evening during the resting phase.  Any ideas why this has started happening?  I am running firmware 1933 (01/08/2015).

Hi Rejuvenation..,

It is not exactly clear (to me) just what is,  or is  not happening,   and just what is the effect of that on  the Classic.

When the Classic transitions to Float,   the Absorb Timer is reset to the Absorb time setting in the Charge menu.   In a normal situation,   this transition to Float occurs before the Classic  Rests.

There is the Auto Reset function,   that when is set to ON,  begins a new day at 23:59,   each day,   and "ReBoots"   the Classic.   Most of us run Classics with ARST =  ON.

You might want to check in the Tweaks menu,   to see if   " ARST "  is set to ON.

What is the situation that you are seeing?

Is the Time Of Day Clock set correctly in your regular Classic (not a Classic Lite)?

Thanks!   Vic
« Last Edit: February 16, 2017, 10:06:22 PM by Vic »
Off Grid - Two systems -- 4 SW+ 5548s, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 3X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes.  Thanks MN for Great Products/Service/Support!

Rejuvenation Farm

  • Newby
  • *
  • Posts: 14
Re: Classic 150's charge times not resetting at night
« Reply #8 on: February 17, 2017, 07:16:05 AM »
Hi Vic,

Thanks for your reply.  ARST was set to "off" on both controllers.  I turned it on for both.  The time and date was correct on both CC's.  I will let you know if this fixed the issue when I get check them tomorrow morning.

Gracias

Vic

  • Hero Member
  • *****
  • Posts: 1614
Re: Classic 150's charge times not resetting at night
« Reply #9 on: February 17, 2017, 03:25:31 PM »
Hi Rejuvenation ..,

Thanks for the info.   Hope that this will help,  please do let us know how you are doing.

Vic
Off Grid - Two systems -- 4 SW+ 5548s, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 3X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes.  Thanks MN for Great Products/Service/Support!

Rejuvenation Farm

  • Newby
  • *
  • Posts: 14
Re: Classic 150's charge times not resetting at night
« Reply #10 on: February 18, 2017, 04:31:10 PM »
That did it - both CC's reset last night.  Thanks guys fr your help.